Thanks heaps MitchD, coincidentally I am now in Canberra too so that might explain why my water started to boil at 98 also. I'll do a wet run and check it out as you described, but where is the PWM% setting?MitchD said:Good to hear you have made some changes and now i'm on a computer and not a phone I can elaborate on my ramblings I posted before.
Now you have changed the boil set point to 99 I would do a "dry run" with your full boil volume for 3 reasons:
1. Check what temperature your water boils at, in Canberra at ~700m above sea level mine boils at 97.5c. If i had it set to 98 or 99 the controller would throw full power at it, however once water is boiling it wont increase in temperature therefore the timer will never start.
You can find this in manual mode by bumping the temperature up a few degrees at a time until it is boiling and the temp sits stable but under your set point. This is your boil set point.
A low setpoint will start the timer but you will only have a gentle simmer, too high and your timer wont start.
2. When you have it at boil you can adjust the PWM% to set how vigorous the boil will be. More % more boil, less % less boil and potentially it will slip under your set point. For a 5500w element i am using 75%
3. With the full boil volume run a 60 minute boil at your temperature setpoint and PWM% and record your boil off. If you stick with a PWM% your boil off will be stable from batch to batch. I boil off 5.5l per hour regardless of it is 10l or 30l.
I'm also running my controller on my Grainfather, I have the mash/boil switch on boil constantly with the idea the controller will regulate the power to the element as required. It has a 2400KW I believe.