Using a second ssr to switch the pump wont fix the problem because it is the 240v causing the scrambling. You may also find that the element switching on and off causes the scramble. If you cant re route your wiring try getting some shielded cable and connext the shield to earth. It may help but if the wiring is that bad it may not either.
 
This isn't true. The element is a resistive load vs an inductive load which has a different pattern for drawing current.

The combination of switching 240v for a motor/pump through a relay on the board causes chatter/arcing which creates the scrambling. SSRs provide isolation between the AC and DC and so would also deal with the issue by removing the 'chatter' and by preventing the 240v from interacting with the board. SSRs (that we are using) also switch at zero on the AC wave, which means even if the SSR switches do 'chatter' its still a 'clean' switch.

So why stick with the current design? It provides flexibility - you can use a DC pump OR an AC pump, it's compact which allows us to fit 2xSSRs in the box for heating which makes the unit great for bigger or faster batches, and it works.

We've tested the boards thoroughly and the emf shielding through the snubber circuit and board design provided has worked with chugger, march and kaixin/kegking pumps without scrambling. But... If you are sloppy with your wiring, then yeah, you might still get issues.

I haven't tried this - but if you really want to use an SSR for the 240v side of the pump, you should be able to run 12v out from the power supply into the relay (pump terminal) on the board and then out to the +ve DC side of the SSR, then run the -ve side of the DC side of the SSR back to the -ve of the power supply. The relay will switch the DC on and off, which will trigger the SSR, which will switch the 240v pump. Please note you can't use a single SSR to switch both heat and pump at the same time.

Or... You could just be neat with your wiring ;)

Of course... If your wiring is neat and you are still having issues - PM me and I'll help.

MitchD said:
Using a second ssr to switch the pump wont fix the problem because it is the 240v causing the scrambling. You may also find that the element switching on and off causes the scramble. If you cant re route your wiring try getting some shielded cable and connext the shield to earth. It may help but if the wiring is that bad it may not either.
 
The ac voltage is the problem. Induced voltage created by the 240v ac is what is causing the scrambling, weather its a resistive or inductive load makes no difference. The use of ssr or relay makes no difference.

If the load side of either the pump or element is ran parallel to the screen wiring it will induce a small amount of ac voltage into that wiring scrambling the screen, turning that ac load off wont fix the scrambled screen because it doesnt have time based reset written into the code.

I'm sure you have done some strenuous testing and you are correct that neat wiring is the way to fix the problem. I wasnt part of you bulk buy because i was impatient and capable of building and assembling it on my own, I built my own by following the schematics posted by matho and max.
While testing (very sloppy wiring) I had a scrambling problem while only using the element run off the same type of ssr you are using.
 
So I called Mitch this morning to chat about this, Mitch was really helpful - here's what we talked about (Mitch feel free to correct / clarify anything).

1. Induced voltage generally occurs when you have two sets of cables running parallel - one with high(er) AC voltage. This will induce a voltage an AC voltage in the lower powered cable nearby. The worst situation (from chatting to Mitch - licensed electrician) is when running high current (Amps) for longer runs (>10m). The principles of - keep wires running parallel either shielded or separated is true in any situation, including the Brauduino. Ideally wires should cross at right angles to reduce induction and the shorter the cable, the smaller the effects.

2. The key issue for screen scrambling in the new Brauduino kit is still the pump. Mitch's setup is a little different in that his LCD is further away from the arduino, with wires running through an electrical cabinet, which means the induction for him was in the wires leading to the LCD as both the element cable and the lcd screen cables were running parallel. It was from his heating element only (no pump involved), however, he runs a 5500w element which is higher than most people and therefore more likely to induce AC in the LCD wires. In the Brauduino kit the LCD is connected with PCB headers, which essentially means the induction is almost impossible to happen in this way (the pins are perpendicular to nearly all the wiring).

3. If your wiring is a mess, with long AC cables and long DC cables, you make yourself more susceptible to EMF both from the pump switching and potentially from the heating elements (though seemingly not very likely with 10A elements being used). Tips - same as given before - keep the wiring short as practically possible, push the wiring down and route it at the back of the box as much as possible. Keep it neat and running around the outside of the box, and DC running separately (not parallel) to the AC cabling. Twist the Pump cables going into the board so they look like a helix with a reasonably tight twist and cable tie them together so they won't come undone (the spiralling helps reduce/cancel the emf around the cord). Twisting the AC cables for the elements going from the SSR to the heat outlet sockets would also potentially assist to cancel any emf/induction.

If your wiring is neat and well run, you will likely find your controller working beautifully for a long time without issues :)

As always - please ask any questions you have and consult with your electrician for verification and advice about anything mentioned here before implementing it.
 
Hi there .
I am interested on making a controller as such ...
I found on the OpenArdbir site 3 pcb designs
GTO Ardbir Controler
PCB Final
PCB OpnArdbir

Which one should I prefer to develop ?
I can find both Arduino Uno and Nano Boards in my country .Other than that ,are all compatible with initial settings of Ardbir?
If I choose to develop the pcb with the arduino nano how is registered at the initial settings?
Thank you in advance.
 
Hi if the arduino nano pcb is worth or I would face problems (I've read on the description that may needed a usb programer (why is that?)) and which one of the two other pcb's provided is best for use with the Arduino uno ...
I need to clarify this before starting gathering parts .
 
Hey guys,

I've got a question, however I'm not sure if this is the correct place to ask it.

I've got the Ardbir all-in-one board and have wired it up following the PDF guide supplied by Ardbir. When I turn it on, everything starts up fine, I can go into manual mode and switch on either the heater or the pump and the LEDs on the board come on. However my SSR does not seem to be activated when I turn switch it on. It's like the terminals on the board get no power despite the LED coming on.

Does anyone have any ideas? Any help would be appreciated.

Thanks
Peter
 
Peter,
I'm not familiar with that particular board, matho's original had the LEDs inline so if they were lit; the on board relay was closed (pump circuit) or there was power to the SSR (heating circuit). Max the poster directly above yours would be able to help you out also a picture of your wiring would be helpful to anyone trying to trouble shoot this. If max hasn't replied in the next day or two send him a pm.

MB
 
MastersBrewery said:
Peter,
I'm not familiar with that particular board, matho's original had the LEDs inline so if they were lit; the on board relay was closed (pump circuit) or there was power to the SSR (heating circuit). Max the poster directly above yours would be able to help you out also a picture of your wiring would be helpful to anyone trying to trouble shoot this. If max hasn't replied in the next day or two send him a pm.

MB
Hi MB, Thanks for the reply. The wiring for the all-in-one board is pretty simple, you kind of just hook it up to the 12v and then hook up the relay...

Here's the image provided by ardbir.
https://s3.amazonaws.com/images.ecwid.com/images/6605042/306558246.jpg

Hopefully I'll hear from Max.
 
ok so circuits look the same/similar; if the LED is lit the Relay out puts should have power, insure you have the board wired to the DC side of the relay, once again a quality pic of your work would be helpful.
Ed: Just a thought you do realise the high voltage side of the relay is just a switch; usually put on the path of the active 240v
 
MastersBrewery said:
ok so circuits look the same/similar; if the LED is lit the Relay out puts should have power, insure you have the board wired to the DC side of the relay, once again a quality pic of your work would be helpful.
Ed: Just a thought you do realise the high voltage side of the relay is just a switch; usually put on the path of the active 240v
Thanks, I understand how the relays work, I built a fermentation chamber with the brewpi system that switches a heater and fridge using similar SSRs.

I can take a pic of my specific wiring when I get home tonight, I'll also double check the output with my meter to make see if there is actually any output coming out or if my heater relays or 12v pump are dead, but it seems unlikely to me that they both would be.

On the curcuits, one thing I notice is that the bus to the LED seems to run in parallel with the bus to the transistor. Is it possible that the transistor, diode or resistors are damaged and so the LED lights up but the circuit breaks down there?
 
Peter, the picture provided by Ardbir has an error. The pump relay is wrong. It illustrates connection form the board and into the 'load' side.
Make sure you connect both the pump relay/SSR to the IN - DC connectors.
 
heffa35 said:
Peter, the picture provided by Ardbir has an error. The pump relay is wrong. It illustrates connection form the board and into the 'load' side.
Make sure you connect both the pump relay/SSR to the IN - DC connectors.
Thanks, yes I get that, but the other relay doesn't work either, nor if I connect my 12v pump directly to the ardbir board as I've read other people do.
 
ok just to make sure all is good I'll post up matho's destructions page 17 is the diagram you want to check out just note his board has a relay onboard for the pump so you will need to wire that through, actually I'd be more inclined to use 2 SSR's but thats just me
View attachment brauduino controller build1.pdf
 
OK, so I broke out the multimeter, when I have the "pump off" I get 11v over the pump terminals, of I have the "pump on" I get 10v over the pump terminals. Both "heat off" and "heat on" give me 0.01v over the heat terminals. This sounds like the transistors are dead?
 
Hi guys, here the status of my controller:
e9chbuz.jpg


PCB mounted and Ardbir running, I made a 3D sketch, feel free to use: https://www.tinkercad.com/things/5at4r51bbMd-caixa

cSRB9sL.png
 
After about 3 months I have finally finished building my controller. I would like to thank Oggie for helping me get started.

I'm super excited to use this in anger for the first time.

20160203_185051.jpg
20160203_185204 - Copy.jpg
 
I have been using my original control box for about 18 months now and run the latest version of ArdBir. I use the original kit that was a board that I had to solder together myself and it has worked brilliantly for the last year and a half.
I had to do a talk today at my brew club (Westgate Brewers) on how to build your own Braumeister type brewery. Everything went pretty well until I opened up the control box. I haven't opened it for a few months and was pretty shocked when I saw what has happened to my SSR.
ssr2.jpgssr1.jpg

I have a 3kw Birko 40l urn and did upgrade the mains connectors to be 20 amp. I very surprised to see how badly cooked the ssr is. A new is on its way from ebay but I think I will have to add some extra cooling to the heatsink when I fit the new ssr.
Has anybody else had a similar issue?
 
Hi Nealk

Yep that does not look the best.

A quick google brings up hits about fake 25A fotek SSRs

It is possible that the SSR you have is not an original?

I actually am still running my original SSRs that I have had for almost 30 years and they are still good but I have a 2000w element.

Regardless of brand SSRs do get hot and there are a few factors that can help.
First is the heatsink. But even mounting direction changes the amount of heat that can be dissipated. Ideal position allows the fins to run vertically and allow convection to create a flow across the heatsink. Heatsink paste is a must. A fan makes an enormous difference. But even the size of the wires connecting to the SSR will change the amount of heat that is dissipated.

I will post the way to tell if is a counterfeit device and note that they have been sold through Amazon and other large retailers not just ebay.

I think the kits have the 40A version and not heard stories about them as yet.

i would consider a bigger heatsink, mounted vertically or a fan when you replace the SSR.
James



Sent from my iPad using Tapatalk HD
 
Hi Nealk

SSR counterfeit 25A Fotek

https://ul.com/newsroom/publicnotices/ul-warns-of-solid-state-relay-with-counterfeit-ul-recognition-mark-release-13pn-52/

there are many other sites and some look to be lower amperage versions relabeled to higher current.

I use other brand ones in my original kit and the latest kit is being set up this week with an Easter brew planned. Fitting a fan will prolong the life of a counterfeit but probably worth checking if you have a 25A version for the beveled corner on the label.

I will check my ones tonight.

James
Zwitter
 
Holy **** man!, I never even thought that it could be counterfeit. Thank you very much for sharing the info. My melted one looks like it is definitely a fake. I have a new one on its way from ebay and the picture shows a genuine one and if that is not what I get I will be very pissed off. This one is coming from Darwin so at least communication will be easier if something goes wrong.
I think I will start a new thread with this information to warn people that they should check their SSR's.
Thanks again James, I really would not even have thought to check this.
Cheers
Neal
 
I use 2 40 amp SSRs both melted using 2400w each. Here's the tip: good heat sink, good thermal contact(quality thermal paste, clean flat contact surfaces, lapping maybe over the top but my next tear down.. ) add a fan. You will then have zero issues.
 
I have a Braudino kit - (Many thanks again for your massive effort Lael) and I've also recently become 'embedded' in Arduino stuff and was wondering where I can get a copy of the sketch for the Braudino - is it straight Ardbir or modified (for reasons best left unasked, I've yet to fire up my Braudino so I don''t know if it straight Ardbir or not )

Cheers
 
Hi eucyblues

The code is "straight" Ardbir which was all originally based on Matho's system

When you go to load it there are some selections in the code you need to make as the basic code supports several versions of boards and display sizes and languages.

The instructions are in the users guide.

There is a youtube showing how it is all done. At this time the code the arduino ships with from Lael is as good as any later version for our purposes.

There is some mucking about with arduinos so unless you are pretty cluey with technical stuff it may be something you can put off for a rainy day? None of it is difficult but for those used to googling answers and downloading etc it is just trial and error.

James

Zwitter

Sent from my iPad using Tapatalk HD
 
Hi guys,

Can someone tell me where I can get the grainfather version of Ardbir? I really need the pump on in manual mode when boiling.

Anyone with the grainfather, what sampletime and windowsize are you using ?

Thanks.
 
Thanks zwitter - much appreciated

When I say embedded in Arduino I really mean it (ask my wife- OMG!!) - for the last few months I've been eating, drinking and sleeping it even on sunny days (at least it feels like it ) So I should be OK

Thanks again

Eb
 
Hey guys, this might be a bit off topic. But i'm looking for the sketchup files for oggies case, has anyone received it? I'm looking at doing my own take on a controller (to do more stuff than just making beer with the grainfather) and as i liked his design i wanted to build on it and modify it, and the STL files, while good for printing a copy, is not really that great for modification.

I've tried contacting Oggie, but have not received any replies, hence my question in this thread.

Andreas
 