In theory there is nothing wrong with switching the neutral if it is a double insulated device. Its when the device has an earthed chasis that it becomes a problem. Now before everyone gets their panties all twisted it is ILLEGAL - AS 1.7.12

AS 1.7.12 STATES " An isolation device shall interupt all active conductors but shall not operate in a neutral conductor, unless permitted by Clause 2.8.2, or an earthing conductor."

AS 2.8.2.2 STATES. " A switch or cct breaker shall not operate in a neutral conductor of -

A. An earth return system

B. Consumer mains.

C. A submain where the neutral is used for earthing of an electrical installation in an outbound building.

D. A submain or final subcircuit in which the neutral conductor is solidly earthed.

The requirements of D. Need not apply to-

i). A multipole switch which includes a contact intended for comnection in the neutral ; or

ii). A switch which is linked with correspinding switches so that the neutral contact cannot remain open when the active contacts are closed.; or

iii). Fire pump control

iv). A multipole switch which is installed for the purpose of conecting an alternate supply.

2.8.2.3 STATES. " Switches in earthing conductors is prohibited.



Edit spellink
 
Ive used the clipsal ones. they are surface mount. 30mm. 4 mounting holes on the terminal blok.

CLI412WE (socket 250v 3p 10 A)

got em at L&H looks like their part No is 6120023800.

josh.
 