I have heard mention a couple of times that it is possible to buy a 15A extension lead & plug the BM into it & chop off the male plug on the other end & wire up a standard 10A plug so you can use it in a standard powerpoint. If nothing is running at the same time from the powerpoint, can you do it?
Wow, lots of uninformed scaremongering going on in this thread :huh:
Bottom line is that legally to do anything more complicated than changing a light globe you need a licensed electrician. I'm not, but I was in exactly the same situation recently as I wanted to run a 3.6kW heating element for my kettle which draws 15A. Because any electrical DIY is illegal in this country I found no reliable info online (but did get find some good discussion on NZ forums where the laws are a bit more "practical"). In the end I got hold of and read AS3000 to make an informed decision on whether to go to Bunnings and spend $10 to make a 15A to 10A adaptor lead.
On page 380, Table C8 details how many 10 and 15 amp points you can have on a single circuit, depending on cable size and breaker rating.
The minimum cross sectional cable area for any power circuit is 2.5mm2 - so lets assume you have this size cable. My interpretation of the table is that if you have a 16 amp circuit breaker (more than likely), you can have one 15A socket outlet and one 10A socket outlet on the same circuit (if you have permanent air-con!).
There are a whole bunch of other requirements in AS3000, but you can only assume your circuits are already installed to the code.
Furthermore, in Appendix C it states:
"For circuits supplying a single item of equipment, the circuit current is simply the nominal load current of the equipment. The circuit conductors and the protective device must have a current carrying
capacity of not less than 16 A (nearest standard rating)."
My solution was to make the adaptor cable and run my 15A element on a circuit with nothing else on it. A couple of dozen brews later and all is fine. The circuit breaker has never tripped and why should it - it's rated at 16A and I'm only drawing 15A. The cable is rated to take the load too.
Again, if you assume your wiring has been done to AS3000, then your circuit breaker is going to trip long before your cables melt. So the worst than can happen if you overload the circuit is you'll trip the breaker. My only recommendation would be to make your cable out of 2.5mm2 cable as a minimum - Bunnings sell some nice heavy orange 3 core cable which does the trick.
Oh yeah, and if your building explodes when you turn the Braumeister on... I was never here
h34r: