Super simple PID controller build/wiring

Australia & New Zealand Homebrewing Forum

Help Support Australia & New Zealand Homebrewing Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

nathanvonbeerenstein

Well-Known Member
Joined
15/11/12
Messages
181
Reaction score
53
Location
wantirna, melbourne
Hi,
Trolled around a bit, but couldn't find any simple wiring diagrams for a PID controller with a probe and the necessary in and out/or heat and cool power sockets. I want to buy OR build one much like the KegKing temp controller, but with a PID controller instead of the STC style one.
Here's the keg King one:
View attachment 85143

Long story short, assembled a herms type system using the keg King controller with the PID but it doesn't learn like a PID does so couldn't hold a stable temperature. I plan to have it control the element in my hlt as the mash recirculates through a 1/2" 50ft chiller in the hlt with the probe at the end of the wort return tube.
It will be mounted the the brew stand I have in the works stylised after the Brew Magic two-tier systems.
Any helps appreciated and all wiring will be checked by an electrician (he works in alarm systems so may not be versed in what I'm trying to achieve I think).

Best and cheapest recommendations much appreciated!

CHEERS!
Nathan
 
Why do you need cooling in a Herms system and how do you expect to cool the hot wort??
 
gap said:
Why do you need cooling in a Herms system and how do you expect to cool the hot wort??
pretty sure they are planning to use the chiller coil as their herms coil

Run the wort through it (instead of water) while it's immersed in their HLT
 
Apologies, should have been more clear when writing this.
I don't have a need or plan for cooling and after further research seems impossible with a simple build like this.
Basically, I just want a temp probe and an AU plug to plug the 2200w element into, and have the PID turn that on and off.
Cheers
 
SBOB said:
pretty sure they are planning to use the chiller coil as their herms coil

Run the wort through it (instead of water) while it's immersed in their HLT
Spot on! Already got 50ft of perfectly good heat exchanger at my fingertips so using that!
 
So exactly what sort of build did you want?

The most complex part of the circuit is the wiring for the LCD display, and some buttons/knob for setting the temperature.
I guess an Up/Down button combo would be fairly simple. Using a smarter LCD (with say SPI comms) reduces the wiring significantly.

I built my own from scratch, it's involved, but not difficult.
 
Basic as hell temperature controller unit:
-1 sestos d1s-Vr-240
-1 power lead to power the unit
-1 ssr with heatsink
-1 output for the 2200w element

I've got all the components as of last night, just need to find the right project housing/junction box from Jaycar and to assemble it.
Does anyone have a wiring diagram for this build?
 
This is from an AHB thread (that I can't find again) it might help.
I'm not an electrician, seek professional input/advice

image.jpeg
 
Benn said:
This is from an AHB thread (that I can't find again) it might help.
I'm not an electrician, seek professional input/advice

attachicon.gif
image.jpeg
Legend!
Thanks mate, that was exactly what I was after!
BUT....
As with most projects undertaken by brewers, it quickly escalated and after research have decided to go all out on a control panel,
Two PID's
Two pump controls
Switchs for almost everything and xlr pt100 probes

Thinking this wiring diagram but with illuminated 6 terminal DPDT rocker switches in place of the button switches:
ImageUploadedByAussie Home Brewer1449873511.221803.jpg

Anyone see any issue with this diagram, such as the substitution of the auber push button switches for eBay rocker switches (rated at 240v 15a)? If not, how would I wire them vs the ones in the wiring diagram?
ImageUploadedByAussie Home Brewer1449873802.296170.jpg

Thanks for the help all [emoji4]
 
booargy said:
Do not wire the E-stop like that. An RCD is not for this purpose.
I will repeat exactly what he said.

Put in a proper emergency stop switch

E-stop is emergency stop...not Earth stop
 
Why don't you just put the element on/off switch in series with the SSR control. That would free up your contactor to use with the E-Stop to drop the mains.
What you have with your e-stop at the moment is more of an earth leakage test button. You could have a button to do this as well as an e-stop if you wanted. Keep in mind that how it is drawn now is with 2 x 1K 1W resistors. At 240V this is 120mA and 28.8W. If it fails to trip the resistors will quickly smoke.
 
Logan_01 said:
Why don't you just put the element on/off switch in series with the SSR control. That would free up your contactor to use with the E-Stop to drop the mains.
What you have with your e-stop at the moment is more of an earth leakage test button. You could have a button to do this as well as an e-stop if you wanted. Keep in mind that how it is drawn now is with 2 x 1K 1W resistors. At 240V this is 120mA and 28.8W. If it fails to trip the resistors will quickly smoke.
Apart from not being a legal way to isolate the element you'll always have voltage on the element if you use the SSR to isolate. Put a contactor or switch on the power, job done
 
I'm gonna be 'that bloke'. Work out what you need from advice here or elsewhere online, then run everything by an electrician regarding the wiring. Then follow their advice, and get them to approve it before you plug it in. That way you're doing it legally and won't hurt yourself or burn down the house now or in the future.
 
Pokey said:
Apart from not being a legal way to isolate the element you'll always have voltage on the element if you use the SSR to isolate. Put a contactor or switch on the power, job done
You are using it to'Control' not to 'Isolate' ... there is a difference. You are correct that you cant legaly 'isolate' through a solid state device, but they can be used for functional(control) switching.
What exactly do you consider the issue with having voltage on the element. The current would be tiny. The only let through would be pico amps from the SCR's / Triacs and pico amps from any snubber circuit in the SSR.
Regardless the insulation of the element would stop you comming into contact with the voltage present anyway. Or does everyone insulate there stock pots from ground and not touch them while their heating?

I don't know anywhere it says you legally need an E-stop anyway(might be wrong as im mainly farmiliar with AS3000, which is mainly for fixed installations).
However where an E-stop is used it must not re-energise the cct upon release of the estop. Gets tricky ay.
 
Thanks for the input fellas, definately not going to put together before I have all the wrinkles ironed out and have already arranged for an experienced sparky to check it, and the components, over before even thinking about plugging it in.

I should have mentioned I did not make this diagram and pulled it of the American forums.
for changes to that diagram. I'm adding a residual current device at the start of the circuitry and installing the emergency stop switch to switch off all power to the board rather than relying on it controlling other components to isolate it for me.
Am I correct in simply having the switch in series at the start of the hot lead to break the circuit all together as I was planning on doing?

As for the complete and mechanical isolation of the element: as per the diagram posted, I plan to have the switch control a mechanical contactor that's normally open when no current runs through it. That way, there is a mechanical isolation when the element switch is off, as well as when the circuit is broken via e-stop, RCD, mains fuse box or inline fuses etc etc etc.
Would this be appropriate?

Cheers for the input
 
Just reading thru this, there seems to be alot of unfamiliarity with electrical wiring in your words. As Wiggman said, pls find a sparky for advice on how to go about this, sometimes forums arent the best method of info especially regarding electricity.Yes, I am an A Grade so I will add here:
An emergency stop switch is usually used to prevent sudden danger - like turning off a conveyor belt before something rolls of it, etc etc. Not for isolation. Keep it simple, just fit a main switch for the whole panel. All my external devices (element, sensors, pumps) are connected via sockets on the bottom of my panel so i can isolate / disconnect for cleaning, moving it, or not in use etc.
This mechanical isolation business sounds unnecessary & over-complicated.

If you in Melbourne I can assist, PM me.
 
Ditchnbeer said:
Just reading thru this, there seems to be alot of unfamiliarity with electrical wiring in your words. As Wiggman said, pls find a sparky for advice on how to go about this, sometimes forums arent the best method of info especially regarding electricity.Yes, I am an A Grade so I will add here:
An emergency stop switch is usually used to prevent sudden danger - like turning off a conveyor belt before something rolls of it, etc etc. Not for isolation. Keep it simple, just fit a main switch for the whole panel. All my external devices (element, sensors, pumps) are connected via sockets on the bottom of my panel so i can isolate / disconnect for cleaning, moving it, or not in use etc.
This mechanical isolation business sounds unnecessary & over-complicated.

If you in Melbourne I can assist, PM me.
Thanks mate, appreciate the offer and info.

As I've said a few times already: I won't be doing anything without fully understanding and the go-ahead by an electrician. Im simply learning at this point and wrapping my head around things. Asking questions helps and I'm fully aware of the dangers electricity poses.

Couldn't i just use the e-stop as that main switch you mentioned At the start of the circuit?
 
So would anyone be able to illustrate the best way to incorporate these into a control box to keep it simple and safe with a wiring diagram?

-Control box power (using e-stop/mushroom dpst switch since I have it?)
-Sestos PID w/ pt100
-40a ssr
-Alarm buzzer
-Element switch (with or without contractor to switch power to element?)
-Din mounted residual current device
-240v pump socket w/switch
-1 Rex-c100 purely as a thermometer (ie controlling nothing)

Would rather go to the electrician with a plan and an idea of wiring.
Cheers
 