Did the fridgie test the 3 pins on the compressor with multi meter.?
Also did he try a new start capacitor as well?
Burnt out compressors, normally just blow the circuit breaker at the power board.
Clicking sound is the overload cutting out due the compressor failing to start.
Most of the time, a new capacitor will solve the issue. If the windings were not tested with a multi meter then it needs to be done on a hermetic system like this.
Try these first before condemning it.
If he went through these tests , then all good. Proballly a seized compressor.
Also did he try a new start capacitor as well?
Burnt out compressors, normally just blow the circuit breaker at the power board.
Clicking sound is the overload cutting out due the compressor failing to start.
Most of the time, a new capacitor will solve the issue. If the windings were not tested with a multi meter then it needs to be done on a hermetic system like this.
Try these first before condemning it.
If he went through these tests , then all good. Proballly a seized compressor.