12A/250Vkunfaced said:A compressor kicking over through a relay isn't ideal, a fridge seems like too big a load to be dropped across the contacts of those tiny relays. Is there a current rating printed on top of them? I can't see it properly in the photos.
Given that the compressor motors are inductive I don't think it's as bad as you might expect when the contacts close as the current takes a few milliseconds to ramp up. The trouble is when the contacts open and there's nowhere for that current to flow, it causes arcing in the relay contacts that can wear them out. Any controller that's been designed to operate an inductive load (like a motor) should have a snubber network included (a resistor and capacitor) across the relay, but this adds cost and takes up more board space so the STC1000's don't have them in my experience.kunfaced said:A compressor kicking over through a relay isn't ideal, a fridge seems like too big a load to be dropped across the contacts of those tiny relays. Is there a current rating printed on top of them? I can't see it properly in the photos.
You never know your luck. I did quickly glance at the case for that reason, and seem to recall it was held together by screws, with nothing stopping a relatively straightforward disassembly. I'll have a closer look when I get home.Michael Burton said:I'd love to see a pic of the internals of the Inkbird but I dare not ask Pataka to rip apart his new acquisition!
Thanks for the info, I hadn't heard of a snubber network before. I use the cooling relay to drop a contactor for my fridge. Probably overkill but my workplace is a great resource.Michael Burton said:Given that the compressor motors are inductive I don't think it's as bad as you might expect when the contacts close as the current takes a few milliseconds to ramp up. The trouble is when the contacts open and there's nowhere for that current to flow, it causes arcing in the relay contacts that can wear them out. Any controller that's been designed to operate an inductive load (like a motor) should have a snubber network included (a resistor and capacitor) across the relay, but this adds cost and takes up more board space so the STC1000's don't have them in my experience.
I've annotated a photo of the old controller I designed way back. Not to gloat, but just to illustrate what components to look for. As you can see they're pretty big when rated for the task and they do add a bit to the build costs. That's why I only included them on the cooling relay and not on the heater relay that will generally never see an inductive load.