Hi Guys,
I've been using the fridgemate to control me ale ferments via a brew belt for the first time. The probe is stuck to the wall of the fermenter and insulated with bubblewrap.
I've set the "set point" to 17C and the differential is set at the minimum value of 1C.
My assumption is that the brew belt should switch off when the temp reaches 18C (17C + 1C differenction), but the "heating light" is still on even 18C is reached. Whats going on here???
If i swich the fridgmate off then on again at this point, the "heating light" then goes away.
I guess I should let it go and see what temp it reaches before the brew belt switched off, but I don't want my ferment reaching 20 degrees or over.
Any comments is appreciated.