Power was off this morning, the main breaker was tripped. Isolated it to the fermenting freezer. Inside had a strong electrical burning smell. Got the fermentors out and found the problem is the defrost circuit. Looks like it has been stuck in defrost mode. The motor side of the defrost timer is open circuit so it's stuffed and the defrost cutoff thermostat is a molten plastic mess, hence the stink. I jumpered the compressor wires and the compressor started up. Yahhh.
It ran nonstop for a full hour and gets cold so it's working again. I got one fermenter into the small backup fridge but the other is just sitting on the bench.
I got another timer and thermostat coming, $30 total delivered, but it will probably take a week or more to get here. Do you recon I can put the fermenting beer back in.
Will bypassing the defrost circuits cause any issues? I just need it at 18C till Sunday maybe then cold crash.
It ran nonstop for a full hour and gets cold so it's working again. I got one fermenter into the small backup fridge but the other is just sitting on the bench.
I got another timer and thermostat coming, $30 total delivered, but it will probably take a week or more to get here. Do you recon I can put the fermenting beer back in.
Will bypassing the defrost circuits cause any issues? I just need it at 18C till Sunday maybe then cold crash.