Been looking at burners lately and have read a few threads on Mongolian burners. I noticed in the pics some are running really clean blue flames, some have more yelow flames; one person said their ring burner was hotter (nothing to do with chilli). Being Mongolian are a low pressure most people are using normal BBQ regs.
LPG has a calorific value around 46.1MJ/kg. Many BBQ regs have a pressure of 2.75kpa (some have 2.8kpa) which is great for Low pressure burners; but the one I was going to use for my burner only has a max flow of 1.5KG/hr. My spare BBQ reg has a max flow of 2.0KG/hr.
Now the
20 Jet Mongolian is rated to 82MJ/hr - 82 / 46.1 = 1.78 KG/hr
23 Jet = 94MJ/hr - 94 / 46.1 = 2.04 KG/hr
32 Jet = 131MJ/hr - 131 / 46.1 = 2.84 KG/hr
So depending on what reg & burner you have you may not be getting the best performance from your burner. A low pressure 2.75kpa reg is available in a 3KG/hr.
Hope this helps.
QldKev
LPG has a calorific value around 46.1MJ/kg. Many BBQ regs have a pressure of 2.75kpa (some have 2.8kpa) which is great for Low pressure burners; but the one I was going to use for my burner only has a max flow of 1.5KG/hr. My spare BBQ reg has a max flow of 2.0KG/hr.
Now the
20 Jet Mongolian is rated to 82MJ/hr - 82 / 46.1 = 1.78 KG/hr
23 Jet = 94MJ/hr - 94 / 46.1 = 2.04 KG/hr
32 Jet = 131MJ/hr - 131 / 46.1 = 2.84 KG/hr
So depending on what reg & burner you have you may not be getting the best performance from your burner. A low pressure 2.75kpa reg is available in a 3KG/hr.
Hope this helps.