IIRC the remaining fuses are there because the CB's from Bunnings won't fit - the other ones have already been changed out. I had a board exactly the same and they were slightly different sizes.


Good to see the RCD - hopefully it's covering everything.


The circuit breakers look like the HPM 16A C curves. If you have your brew element(s) on one of these you can draw 20-30A for a couple of seconds but more than this will trip out straight away.


This is enough to cover elements turning on (probably 14-15A for a 2400W) but your fuses are an unknown - they may trip straight away or may allow too much for the  wiring at continuous load.