  1. We have implemented the ability to gift someone a Supporting Membership now! When you access the Upgrade page there is now a 'Gift' button. Once you click that you can enter a username to gift an account Upgrade to. Great way to help support this forum plus give some kudos to anyone who has helped you.
    Dismiss Notice

Splitting a 20A socket

Discussion in 'Electronics, Hardware & Software' started by sixfignig, 16/11/18.

 

  1. sixfignig

    Well-Known Member

    Joined:
    26/10/15
    Messages:
    127
    Likes Received:
    31
    Gender:
    Male
    Location:
    Gold Coast
    Posted 16/11/18
    I have a single socket 20A circuit installed in my garage, which is placed conveniently for brewing.

    I'd love to be able to use it to power two separate 10A appliances (a 2200w element, and a 2200w element through a Grainfather Controller).

    Is it possible to have a qualified sparky knock up a "site powerboard" type of device that will allow me to achieve the above? I preferably don't want to change the physical wall socket as I have other devices I need to use it for.
     
  2. captain crumpet

    Well-Known Member

    Joined:
    24/4/17
    Messages:
    268
    Likes Received:
    126
    Gender:
    Male
    Posted 16/11/18
    so you want something that plugs into your 20a socket, which has 2x 10a sockets?

    as long as it only plugs in and isn't permanent wiring, and the cables match the same size as the 20a subcircuit it shouldn't be a problem.
     
  3. Bonenose

    Well-Known Member

    Joined:
    22/1/17
    Messages:
    228
    Likes Received:
    51
    Gender:
    Male
    Location:
    Darwin
    Posted 16/11/18
    It is possible but it is also pushing the limits of a single circuit.
    I am assuming it is a single phase circuit.
     
  4. sixfignig

    Well-Known Member

    Joined:
    26/10/15
    Messages:
    127
    Likes Received:
    31
    Gender:
    Male
    Location:
    Gold Coast
    Posted 16/11/18
    Yes, that's correct.

    Mind my ignorance but why is it pushing the limits of a single circuit? The total draw would be ~ 4400w through a single 20A socket (which is rated to 4800w @ 240V)
     
  5. Bonenose

    Well-Known Member

    Joined:
    22/1/17
    Messages:
    228
    Likes Received:
    51
    Gender:
    Male
    Location:
    Darwin
    Posted 16/11/18
    You have any dodgy connections on that circuit and you are going to start melting stuff.
     
  6. n87

    Same as it ever was

    Joined:
    30/4/14
    Messages:
    1,753
    Likes Received:
    420
    Gender:
    Male
    Location:
    NSW
    Posted 16/11/18
    You should be able to plug a 10A plug into a 20A socket, they are designed to be able to do this.
    Maybe a long shot, but maybe look for a 20A powerboard... I cant imagine the do exist tho, once you get that high you tend to have dedicated sockets.


    Didnt think of if you had round pin 20A, in which case there are things like this: http://www.seltec.com.au/Product-Ca...Output-13-Pin-AUS-20A-Captive-Plug-Input.html

    Not going to be cheap tho.
     
    Last edited: 16/11/18
  7. Coalminer

    Well-Known Member

    Joined:
    20/3/08
    Messages:
    374
    Likes Received:
    129
    Gender:
    Male
    Location:
    Lake Macquarie N.S.W.
    Posted 16/11/18
    Same with any circuit.
    The whole idea of a 20amp circuit is to carry 20 amp i.e. 4800 watts safely
     
    mischa6262 likes this.
  8. Bonenose

    Well-Known Member

    Joined:
    22/1/17
    Messages:
    228
    Likes Received:
    51
    Gender:
    Male
    Location:
    Darwin
    Posted 16/11/18
    I have replaced too many melted plugs and outlets etc. over the years. Yes it should work but I would advise some caution.
     
  9. captain crumpet

    Well-Known Member

    Joined:
    24/4/17
    Messages:
    268
    Likes Received:
    126
    Gender:
    Male
    Posted 16/11/18
    maybe if he were trying to pull 20a out of a 10a gpo
     
  10. koshari

    Well-Known Member

    Joined:
    4/5/17
    Messages:
    454
    Likes Received:
    155
    Posted 16/11/18
    What you are seeking can be easily done. Get a sparky to wire up some 10a outlets individually protected with 10a breakers fed from the 20a plug. This way you have effectively maximim demand by limitation. And under no circumstances would you then be able to overload either the 20a plug/socket or either of the 10a ones.

    Prolly cost about 100 bucks in parts and an hours labour.
     
    mischa6262 likes this.
  11. azzachaz

    Member

    Joined:
    6/2/19
    Messages:
    5
    Likes Received:
    0
    Gender:
    Male
    Location:
    Canberra
    Posted 21/2/19
    Wouldn't it be simpler to just replace the single GPO outlet with a double? (rated to 20A)
     
  12. Maheel

    Well-Known Member

    Joined:
    19/1/10
    Messages:
    1,910
    Likes Received:
    175
    Posted 21/2/19
    but you cold not pull 2 x 20amp from it and he said wants to leave it as a 20amp
    better to make the "box" Koshari suggested

    I run these for 15amp (round pin) and dont melt plugs like has happened in the past.
    Worth the investment if you can i reckon
    http://rover.ebay.com/rover/1/705-5...0001&campid=5338413729&icep_item=173499614554
     
  13. Muzzaguzza

    Member

    Joined:
    15/9/18
    Messages:
    8
    Likes Received:
    1
    Gender:
    Male
    Location:
    Port Hedland
    Posted 24/2/19
    Seriously Bonenose. Best not to say anything if you're not too sure about what you're talking about. A 20 amp outlet is rated at exactly that, 20 amps. Unless the last 35 years of being a sparky, I've been getting it all wrong. The cable is rated at 20 amps along with the outlet and the RCD/MCB.
     
    pnorkle likes this.
  14. Bonenose

    Well-Known Member

    Joined:
    22/1/17
    Messages:
    228
    Likes Received:
    51
    Gender:
    Male
    Location:
    Darwin
    Posted 25/2/19
    That is obviously why I keep replacing melted plugs and outlets on 15 and 20 amp circuits
     
  15. Muzzaguzza

    Member

    Joined:
    15/9/18
    Messages:
    8
    Likes Received:
    1
    Gender:
    Male
    Location:
    Port Hedland
    Posted 27/2/19
    Would it ever occur to you it's not the circuit, but what you're plugging into it? If i plugged in a coat hanger into the active and neutral - would it be the circuit's fault it would trip the breaker or blow up in your face if you had no circuit protection????

    My previous statement stands.
     
  16. Bonenose

    Well-Known Member

    Joined:
    22/1/17
    Messages:
    228
    Likes Received:
    51
    Gender:
    Male
    Location:
    Darwin
    Posted 27/2/19
    That was always my point.
     
  17. Muzzaguzza

    Member

    Joined:
    15/9/18
    Messages:
    8
    Likes Received:
    1
    Gender:
    Male
    Location:
    Port Hedland
    Posted 27/2/19
    Sorry mate. I can't keep this going because there's an old saying and i'm not going to say it. Keep well.
     
  18. krz

    Well-Known Member

    Joined:
    30/5/14
    Messages:
    159
    Likes Received:
    37
    Posted 27/2/19
    <hint>
    Usually your oven circuit will be on something like 25A.
    Its probably hardwired, but you can buy a plug/socket that is rated 25A, swap it, then run an extension lead top your brew kit.
    </hint>
     
  19. azzachaz

    Member

    Joined:
    6/2/19
    Messages:
    5
    Likes Received:
    0
    Gender:
    Male
    Location:
    Canberra
    Posted 28/2/19
    This doesn't solve the problem of needing 2 points. Unless you are suggesting a 25A double outlet and running 2 extension leads?
     