15a Plug On 40l Birko

Aussie Home Brewer

Help Support Aussie Home Brewer:

kierent

Well-Known Member
Joined
2/8/09
Messages
158
Reaction score
8
Hi

I recently bought a 2nd hand 40L birko urn for BIAB. I got it and the plug is a 15A plug that has had the earth pin tampered with so it will fit in a normal 10A socket. (I think that's what normal house power points are?).


The label on the bottom of the urn says 240-250V and 12.5A. Is this safe to use in my home? Seems a bit dodgy. I'll ask the lady tomorrow what the go with it is but thought some one on here might know whether it's safe?
Thanks

photo.jpg
 

pokolbinguy

The Pokolbin Brewhaus and Winery.
Joined
7/4/06
Messages
3,027
Reaction score
11
is there a label or anything on the urn itself? it 'may' be a 10A unit but the plug got damaged and someone botched it up. but that is a big maybe
 

NickB

I haven't had a C**t all night, Drinkstable....
Joined
29/6/06
Messages
4,436
Reaction score
191
No, get a qualified sparky to replace the plug and install a 15A socket for you.

Cheers
 

adryargument

Well-Known Member
Joined
27/1/11
Messages
878
Reaction score
83
That earth pin looks dodgy as / grinded?
Anything 2400w is 10amp.
 

kierent

Well-Known Member
Joined
2/8/09
Messages
158
Reaction score
8
I suppose it's fair enough, on the label that says 12.5A it says 3000W. Pretty hefty.
 

kierent

Well-Known Member
Joined
2/8/09
Messages
158
Reaction score
8
That earth pin looks dodgy as / grinded?
Anything 2400w is 10amp.
Yeah, they've used a grinder or something so it will fit in a 10A socket. I'll get it fixed by a sparky. Thanks for the advice
 

adryargument

Well-Known Member
Joined
27/1/11
Messages
878
Reaction score
83
Yeah, they've used a grinder or something so it will fit in a 10A socket. I'll get it fixed by a sparky. Thanks for the advice
IMO don't bother fixing the pin, make sure you have a 3000w socket first.
 

seemax

Well-Known Member
Joined
9/4/08
Messages
1,199
Reaction score
5
The circuit will probably take the load... but the GPO is only rated at 10A. Get a sparky ... dedicated 15A circuit is the go!
 

NealK

Well-Known Member
Joined
28/2/12
Messages
400
Reaction score
150
I bought an urn from graysonline that was sold as 10 amp but had a 15 amp plug on it. I did some research and found out I had the 3000w version which needs a 15 amp socket. Fortunately I have a 1970's (possibly older than me!) jacuzzi that has a 15 amp socket for the heating element. I had to buy a 15amp extension cord (the socket is in a bad spot), but it works very well. If yours is the 3000w element and not the 2400w then you are going to need an electrical circuit that can handle it.
I have not seen the 2400w urn in action but I definitely get a very strong boil and have no complaints about my urn.

I hope this helps.
 

stux

Hacienda Brewhaus
Joined
15/12/09
Messages
2,978
Reaction score
310
I'd count myself lucky to score a 3000W urn :)

Have you checked if you have a 15A socket in your circuit box? Or perhaps where an old a/c used to be?
 

Bribie G

Adjunct Professor
Joined
9/6/08
Messages
19,838
Reaction score
4,393
The 2400W Birko is good but the 3000 is the dux - well worth investigating the 15a circuit. In any case the 2400 can trip some 10a circuits as it is, if there are already a few appliances on it anyway. In an old place if a couple of ferm fridges kicked in at the same time and a magpie flew overhead then zap.
 

kierent

Well-Known Member
Joined
2/8/09
Messages
158
Reaction score
8
I'd count myself lucky to score a 3000W urn :)

Have you checked if you have a 15A socket in your circuit box? Or perhaps where an old a/c used to be?
Yeah I was thinking that after I realised it was 3000W. It seems most are 2400W and some have complained about it taking a while to boil. So I'm stoked I got a 3000W model. I haven't had a look to see if I have a 15A circuit but we have an air conditioner so I reckon we would. When I get the 15A socket put in I'll ask the sparky about the plug
 

bradsbrew

Who's up for a pint?
Joined
22/5/08
Messages
0
Reaction score
4
Hi

I recently bought a 2nd hand 40L birko urn for BIAB. I got it and the plug is a 15A plug that has had the earth pin tampered with so it will fit in a normal 10A socket. (I think that's what normal house power points are?).


The label on the bottom of the urn says 240-250V and 12.5A. Is this safe to use in my home? Seems a bit dodgy. I'll ask the lady tomorrow what the go with it is but thought some one on here might know whether it's safe?
Thanks
I would be contacting whoever put the testntag label on it and ask them how it passed.
 

barls

causer of chaos and mayhem
Joined
30/1/05
Messages
6,167
Reaction score
784
I would be contacting whoever put the testntag label on it and ask them how it passed.
i second that, failing that maybe contact the authority who looks after the tagging and see what they say about it. one of the things to look for when tagging is dodgy plugs.
 

booargy

Well-Known Member
Joined
16/6/10
Messages
680
Reaction score
71
I would say whoever sold it cut the pin to see if it worked.
 

pcmfisher

Well-Known Member
Joined
21/11/07
Messages
1,259
Reaction score
232
Grinding earth pins - what a disgrace.
I would have just chopped it off....... :ph34r: :ph34r:
 

komodo

Well-Known Member
Joined
24/9/08
Messages
1,409
Reaction score
35
I would have just lopped the end off and stuck a 10amp plug end on. Power circuit will be 16amp any way.
As for the test tag - who said the pin was filed down when the tag was put on? Might have been fine when it was tagged. Then the test and tag guy left pin was ground down. People do it all the time which is why they whole test and tag thing is a joke - especially when industry isnt required to retrofit RCDs to existing power circuits.
 

kierent

Well-Known Member
Joined
2/8/09
Messages
158
Reaction score
8
I would have just lopped the end off and stuck a 10amp plug end on. Power circuit will be 16amp any way.
As for the test tag - who said the pin was filed down when the tag was put on? Might have been fine when it was tagged. Then the test and tag guy left pin was ground down. People do it all the time which is why they whole test and tag thing is a joke - especially when industry isnt required to retrofit RCDs to existing power circuits.
I actually had a look on the meter box today and it looks like most of the circuits are 10A circuits to power points. There is a 16A circuit for the a/c but that's hardwired rather than into a socket. There were a few other 16A circuits and a 12.5A circuit which is what the urn is rated at so if I can figure out where those outlets are I'm good to go with a 10A plug end. Or a 15A extension cord.... Time to call the sparky, don't really wanna electrocute myself/burn the house down. Or even have to keep resetting circuit breakers mid-boil. That would kill my IBU calculations :)
 

glenwal

aus Bier hergestellt
Joined
8/12/10
Messages
812
Reaction score
29
I actually had a look on the meter box today and it looks like most of the circuits are 10A circuits to power points. There is a 16A circuit for the a/c but that's hardwired rather than into a socket. There were a few other 16A circuits and a 12.5A circuit which is what the urn is rated at so if I can figure out where those outlets are I'm good to go with a 10A plug end. Or a 15A extension cord.... Time to call the sparky, don't really wanna electrocute myself/burn the house down. Or even have to keep resetting circuit breakers mid-boil. That would kill my IBU calculations :)

Normal power circuits (normally) have 16A breakers. If you have 10A (or 12.5A) breakers they will be for lights.

BUT, the GPO (power point) is only rated at 10A, so if you plug it into a standard power point you run the (small) risk of the outlet overheating, melting and burning your house down (and all without tripping the breaker).


Calling a sparky to install a dedicated 15A GPO is your best bet.
 

kierent

Well-Known Member
Joined
2/8/09
Messages
158
Reaction score
8
Ended up getting a 15A socket installed on the AC wiring. Boils like a beast, I have had to add water to every brew because it evaporates so much. But that's cool. I have searched this question and I think it's ok, but does anyone know if having a boil that's really vigorous will actually over bitter my brew? I haven't noticed the brews are over bittered but theoretically, is a rolling boil preferable to a vigorous boil? (even though those terms are relative). I don't mind adding water, just don't wanna over bitter.
 